0x04018000
Blade voltage fault.

Explanation

Blade CPU has encountered voltage fault.

Severity

Error

Alert Category

Blades (Critical) - mmTrapBladeC

Log Source

Blade_##

Automatically notify service

No

Recoverable

Yes

Alarm Panel LED (BC T and BC HT)

Critical

User response

Perform these steps:
  1. Check the event log to see if this is happening on multiple blades, suspect the power module, not the blade server.
    1. Identify the power module that is causing the problem (the AC or DC LED is not lit).
      Note: If you cannot easily identify which power module is bad, you should schedule downtime before going further.
    2. Remove the power module in the power domain that powers the failing blade servers, one power module at a time.
    3. Wait 5 minutes.
    4. If the issue persists, swap the other power module in the power domain.
  2. If this is happening for a single blade server:
    1. Reseat the blade server.
    2. Update the firmware for the blade server through the advanced management module Web interface (go to Blade Tasks).
    3. Replace the system board (trained service technician only).