Blade voltage fault.
Explanation
Blade CPU has encountered voltage fault.
Severity
Error
Alert Category
Blades (Critical)
-
mmTrapBladeC
Log Source
Blade_##
Automatically notify service
No
Recoverable
Yes
Alarm Panel LED (BC T and BC HT)
Critical
User response
Perform these steps:
- Check the event log to see if this is happening on multiple blades, suspect the power module, not the blade server.
- Identify the power module that is causing the problem (the AC or DC LED is not lit).
Note: If you cannot easily identify which power module is bad, you should schedule downtime before going further.
- Remove the power module in the power domain that powers the failing blade servers, one power module at a time.
- Wait 5 minutes.
- If the issue persists, swap the other power module in the power domain.
- If this is happening for a single blade server:
- Reseat the blade server.
- Update the firmware for the blade server through the advanced management module Web interface (go to Blade Tasks).
- Replace the system board (trained service technician only).