0x0421D081
CPU 01 over temperature

Explanation

The service processor has detected that the CPU has exceed a critical thermal threshold(overheating due to an overload).

Severity

Error

Alert Category

Blades (Critical) - mmTrapBladeC

Log Source

Blade_##

Automatically notify service

No

Recoverable

Yes

Alarm Panel LED (BC T and BC HT)

Critical

User response

Perform these steps:
  1. Check the room ambient temperature to ensure that it is within the operating specifications for the chassis.
  2. Make sure that all fan/blower modules are running. Replace fan modules if necessary.
  3. Make sure that a device or filler is installed in each bay in the front and rear of the chassis, and make sure that there is nothing covering the bays. Any missing components can cause a major reduction in airflow for the blade server.
  4. Make sure that there is nothing covering the media tray (that will disrupt the airflow to the ambient temperature sensor).
  5. Update the firmware for the advanced management module. You can find firmware on the IBM BladeCenter software and device drivers Web page.
  6. Update the firmware for the blade server.
  7. For all blade servers other than the JSxx blade servers, make sure the heat sink and CPU are secured on the system board.
    Note: Be careful when handling the heat sink and CPU, they may be extremely hot.
  8. Check the IBM Support Web page for any service bulletins that might be related to this problem.