0x08238004
Power module 04 48V over current fault

Explanation

The current in the specified power module exceeded the current fault threshold.

Severity

Error

Alert Category

Power Modules (Critical) - mmTrapPsC

Log Source

Power_##

Automatically notify service

Yes

Recoverable

Yes

Chassis LED

Error

Alarm Panel LED (BC T and BC HT)

Critical

User response

Perform these steps:
  1. Reseat the power module.
  2. Check the event log for other system devices that might be having a similar problem, which might indicate that the problem was caused by an external short. If no external short is found, replace the power module.
  3. If the problem persists, verify that you have a stable power input source.
    Note: (DC Current) Only trained service personnel, other than IBM service technicians, are authorized to make the connections to and disconnections from the -48 volt DC power source. IBM service technicians are not certified or authorized to install or remove the -48 volt power cable. The customer is responsible for ensuring that only trained service personnel install or remove the -48 volt power cable.