The integrated management module (IMM) consolidates the service processor functionality, video controller, and remote presence capabilities in a single chip on the system board. The IMM monitors all components of the blade server and posts events in the IMM event log. In addition, most events are also sent to the advanced management module event log.

The following table lists IMM error messages that are displayed in the advanced management module event log and suggested actions to correct the detected problems. These events, in a slightly different format, are also displayed in the IMM event log.
Note: An updated list of IMM error messages and corrective actions are available on the IBM website at http://www.ibm.com/systems/support/supportsite.wss/docdisplay?lndocid=MIGR-5079339&brandind=5000008.
  • Follow the suggested actions in the order in which they are listed in the Action column until the problem is solved.
  • See Parts listing - BladeCenter HX5 to determine which components are CRUs and which components are FRUs.
  • If an action step is preceded by "(Trained service technician only)," that step must be performed only by a trained service technician.
Type Error Message Action
Error Code: 0x80010200
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error System board (Planar 12V) voltage under critical threshold. Reading: X, Threshold: Y
  1. If the under voltage problem is occurring on all blade servers, look for other events in the log related to power and resolve those events (see Event logs).
  2. View the event log provided by the advanced management module for your BladeCenter chassis and resolve any power related errors that might be displayed.
  3. If other modules or blade servers are logging the same issue, check the power supply for the BladeCenter chassis.
  4. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error System board (Planar 5V) voltage under critical threshold. Reading: X, Threshold: Y
  1. Remove all expansion cards from the blade server (see Removing an I/O expansion card).
  2. Remove all storage drives from the blade server (see Removing a solid state drive).
  3. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error System board (Planar 3.3V) voltage under critical threshold. Reading: X, Threshold: Y
  1. Remove all expansion cards from the blade server (see Removing an I/O expansion card).
  2. Remove all storage drives from the blade server (see Removing a solid state drive).
  3. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Code: 0x80010201
Error CMOS Battery (CMOS Battery) voltage under critical threshold. Reading: X, Threshold: Y Replace the system battery (see Removing the battery and Installing the battery).
Error Code: 0x80010900
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error System board (Planar 12V) voltage over critical threshold. Reading: X, Threshold: Y
  1. If the over voltage problem is occurring on all blade servers, look for other events in the log related to power and resolve those events.
  2. View the event log provided by the advanced management module for your BladeCenter chassis and resolve any power-related errors that might be displayed.
  3. If other modules or blade servers are logging the same issue, check the power supply for the BladeCenter chassis.
  4. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error System board (Planar 5V) voltage over critical threshold. Reading: X, Threshold: Y
  1. Remove all expansion cards from the blade server (see Removing an I/O expansion card).
  2. Remove all storage drives from the blade server (see Removing a solid state drive).
  3. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error System board (Planar 3.3V) voltage over critical threshold. Reading: X, Threshold: Y (Trained service technician only) Replace the system board (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Code: 0x80030100
Information Group 1, memory (Mem Lane Spared) occurred/recovered.

Information only.

Error Code: 0x80070100
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Warning Expansion Module X, (BPE4_Y Slot Z) bus uncorrectable error
Note:
  1. X = Module number
  2. Y = BPE4 ID (1, 2, 3, or 4). The max BPE4 number is 4, and there are 2 slots in each BPE4. Module number is based on the configuration of the BPE4
  1. Update the firmware for the service processor (BMC), BIOS, and firmware for the advanced management module.
  2. Reseat the memory DIMMs (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
  3. Reseat any expansion cards that are installed (see Removing an I/O expansion card and Installing an I/O expansion card).
  4. (Trained service technician only) Replace the system board (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Warning Group 2, (PCI express bus X, Expansion Module Y) firmware progress (I/O Resources) warning
Note:
  1. X = PCI slot (1, 2, or 3)
  2. Y = Module number (0, 1, or 2)
To allow more PCIe space, choose one of the following steps:
  • Change MM configuration setting to 1 GB.
    1. In the Setup utility, click System Settings > Devices and I/O Ports > MM Config Base.
    2. Set MM Config Base to 1 GB.
  • Enable PCI 64-bit resource.
    1. In the Setup utility, click System Settings > Devices and I/O Ports > PCI 64-Bit Resource.
    2. Enable PCI 64-Bit Resource.
Warning Processor X, temperature (CPU X OverTemp) warning [Note: X=1-2]
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all of the fans on the BladeCenter chassis are running.
Warning System board, temperature (Inlet Temp) warning
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all of the fans on the BladeCenter chassis are running.
Warning System board, temperature (MEU Overtemp) warning
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all of the fans on the BladeCenter chassis are running.
Warning Memory device X, temperature (DIMM X) warning [Note: X=1-16]
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all of the fans on the BladeCenter chassis are running.
Warning Memory deviceX, temperature (MEU DIMM X) warning [Note: X=1-24]
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all of the fans on the BladeCenter chassis are running.
Error Code: 0x80070200
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error Chassis, processor (CPU Cooling) critical
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all the fans are on the BladeCenter chassis are running (see the documentation for your BladeCenter chassis).
  4. Make sure Acoustics mode is not enabled on the BladeCenter chassis (see the documentation for your BladeCenter chassis).
  5. (Trained service technician only) Make sure that the microprocessor heat sink is properly attached to the CPU (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
  6. Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
Error Expansion Module X, Expansion Card (BPE4_Y Fault) critical
Note:
  1. X = Module number
  2. Y = BPE4 ID (1, 2, 3, or 4). The max BPE4 number is 4, and there are 2 slots in each BPE4. Module number is based on the configuration of the BPE4
  1. Reseat the blade expansion unit (see Removing an expansion unit and Installing an expansion unit).
  2. Replace the blade expansion unit (see Removing an expansion unit and Installing an expansion unit).
Error Processor X, temperature (CPU X OverTemp) critical [Note: X=1-2]
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all of the fans on the BladeCenter chassis are running.
  4. (Trained service technician only) Make sure that the microprocessor heat sink is properly attached to the CPU (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
  5. (Trained service technician only) Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
Error Memory device X, temperature (DIMM X Temp) critical [Note:X=1-16]
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all of the fans on the BladeCenter chassis are running.
  4. (Trained service technician only) Make sure that the microprocessor heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
Error Memory device X, temperature (MEU DIMM X Temp) critical [Note:X=1-24]
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all of the fans on the BladeCenter chassis are running.
  4. (Trained service technician only) Make sure that the microprocessor heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
Error Group 1 (mem dev 1-40) memory (MEU Mem Lane) critical
  1. Reseat the IBM MAX5 expansion blade (see Removing an IBM MAX5 expansion blade and Installing an IBM MAX5 expansion blade).
  2. Replace the IBM MAX5 expansion blade (see Removing an IBM MAX5 expansion blade and Installing an IBM MAX5 expansion blade).
Error System board, voltage (Planar Fault) critical
  1. Reseat the blade server in the BladeCenter chassis (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
  2. Remove the blade server from the BladeCenter chassis and install an identical known good blade server in the BladeCenter chassis (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis). If the problem is related to a power supply, replace the power supply.
  3. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error System board, temperature (Inlet Temp) critical
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all of the fans on the BladeCenter chassis are running.
Error Proc/IO module 1, temperature (IOH Temp) critical
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all of the fans on the BladeCenter chassis are running.
Error System board, chip set (Sys Board Fault) critical
  1. Make sure that the latest firmware is being used (see Updating firmware and device drivers).
  2. Reset the UEFI firmware settings to default values using the Setup utility (see Using the Setup utility).
  3. Reseat the blade server in the BladeCenter chassis (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
  4. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Processor X, interconnect (CPU X Int Link) critical [Note: X=1-2]
  1. Remove the blade server and ensure the processors are installed correctly (see Installing a microprocessor and heat sink).
  2. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  3. Verify that the scalability card is installed correctly (see Removing the 2-node scalability card and Installing the 2-node Scalability card, or see Removing the 1-node speed burst card and Installing the 1-node speed burst card).
  4. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
  5. (Trained service technician only) Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
  6. Replace the scalability card (see Removing the 2-node scalability card and Installing the 2-node Scalability card, or see Removing the 1-node speed burst card and Installing the 1-node speed burst card).
  7. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Interconnect X, connector (Ext QPI Link X) critical [Note: X=1-4]
  1. Remove the blade server and ensure the processors are installed correctly (see Installing a microprocessor and heat sink).
  2. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  3. Verify that the scalability card is installed correctly (see Removing the 2-node scalability card and Installing the 2-node Scalability card, or see Removing the 1-node speed burst card and Installing the 1-node speed burst card).
  4. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
  5. (Trained service technician only) Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
  6. Replace the scalability card (see Removing the 2-node scalability card and Installing the 2-node Scalability card, or see Removing the 1-node speed burst card and Installing the 1-node speed burst card).
  7. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error PCI express bus 1, Expansion Card (CFFh Exp) critical
  1. Check the operating-system event log and the system-event log because it might contain additional information (see Event logs).
  2. Update the device drivers for the CFFh expansion card.
  3. Reseat the blade server in the BladeCenter chassis (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
  4. Reseat the expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
  5. Replace the expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
Error PCI express bus 2, Expansion Card (CIOh Exp 2 Fault) critical
  1. Check the operating-system event log and the system-event log because it might contain additional information (see Event logs).
  2. Update the device drivers for the CIOh expansion card.
  3. Reseat the blade server in the BladeCenter chassis (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
  4. Reseat the expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
  5. Replace the expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
Error PCI express bus 3, Expansion Card (CIOv Exp Fault) critical
  1. Check the operating-system event log and the system-event log because it might contain additional information (see Event logs).
  2. Update the device drivers for the CIOv expansion card.
  3. Reseat the blade server in the BladeCenter chassis (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
  4. Reseat the expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
  5. Replace the expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
Error Code: 0x80070300
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error Expansion Module X, temperature (BPE4_Y TMP) non-recoverable
Note:
  1. X = Module number
  2. Y = BPE4 ID (1, 2, 3, or 4). The max BPE4 number is 4, and there are 2 slots in each BPE4. Module number is based on the configuration of the BPE4
  1. Check the room ambient temperature to ensure that it is within the operating specifications for the chassis (see Features and specifications).
  2. If an air filter is installed, make sure that it is cleaned or replaced (see the documentation for your BladeCenter chassis).
  3. Make sure that all fan/blower modules are running. Replace fan modules if necessary (see the documentation for your BladeCenter chassis).
  4. Make sure that a device or filler is installed in each bay in the front and rear of the chassis, and make sure that there is nothing covering the bays. Any missing components can cause a major reduction in airflow for the blade server (see the documentation for your BladeCenter chassis).
  Expansion Module X, voltage (BPE4_Y VOL) non-recoverable
Note:
  1. X = Module number
  2. Y = BPE4 ID (1, 2, 3, or 4). The max BPE4 number is 4, and there are 2 slots in each BPE4. Module number is based on the configuration of the BPE4
  1. Check the room ambient temperature to ensure that it is within the operating specifications for the chassis (see Features and specifications).
  2. If an air filter is installed, make sure that it is cleaned or replaced (see the documentation for your BladeCenter chassis).
  3. Make sure that all fan/blower modules are running. Replace fan modules if necessary (see the documentation for your BladeCenter chassis).
  4. Make sure that a device or filler is installed in each bay in the front and rear of the chassis, and make sure that there is nothing covering the bays. Any missing components can cause a major reduction in airflow for the blade server (see the documentation for your BladeCenter chassis).
Error Processor X, temperature (CPU X OverTemp) non-recoverable [Note: X=1-2]
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all of the fans on the BladeCenter chassis are running.
  4. Make sure that each bay of the BladeCenter chassis contains either a device or a filler.
  5. Make sure that the blade server is not missing any heat sinks, DIMMs, or heat-sink fillers (see Parts listing - BladeCenter HX5).
  6. (Trained service technician only) Make sure that the microprocessor heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
Error System board, temperature (Inlet Temp) non-recoverable
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all of the fans on the BladeCenter chassis are running.
  4. Make sure that each bay of the BladeCenter chassis contains either a device or a filler.
  5. Make sure that the blade server is not missing any heat sinks, DIMMs, or heat-sink fillers (see Parts listing - BladeCenter HX5).
  6. (Trained service technician only) Make sure that the microprocessor heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
Error Proc/IO module 1, temperature (IOH Temp) non-recoverable
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all of the fans on the BladeCenter chassis are running.
  4. Make sure that each bay of the BladeCenter chassis contains either a device or a filler.
  5. Make sure that the blade server is not missing any heat sinks, DIMMs, or heat-sink fillers (see Parts listing - BladeCenter HX5).
  6. (Trained service technician only) Make sure that the microprocessor heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
Error Code: 0x80070600
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error Processor X, temperature (CPU X OverTemp) non-recoverable [Note: X=1-2]
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all of the fans on the BladeCenter chassis are running.
  4. Make sure that each bay of the BladeCenter chassis contains either a device or a filler.
  5. Make sure that the blade server is not missing any heat sinks, DIMMs, or heat-sink fillers (see Parts listing - BladeCenter HX5).
  6. (Trained service technician only) Make sure that the microprocessor heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
Error System board, interconnect (Pwr Share Jumper) non-recoverable
  1. Reseat the cap on the power sharing connector (see Blade server connectors - BladeCenter HX5).
  2. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Code: 0x80090000
Information System board, memory (Performance Mode) disabled/enabled This is informational only, no action is required. The performance mode has been enabled or disabled.
Error Code: 0x800B0100
Error Group 1, memory (Bckup Mem Status) is not redundant
  1. Check the event logs for other memory errors that might occur (see Event logs).
  2. Reseat all of the memory modules in the blade server (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
  3. Make sure all of the memory is enabled in the Setup utility (see Using the Setup utility). Notice which memory modules are disabled before you continue to the next step.
  4. Replace the memory modules that were disabled in the Setup utility (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
  5. (Trained service technician only) Replace the microprocessor that controls the failing memory module.
    Note: DIMM connectors 1 through 8 are controlled by the first microprocessor and DIMM connectors 9 through 16 are controlled by the second microprocessor.
    See Removing a microprocessor and heat sink and Installing a microprocessor and heat sink.
Error Code: 0x800B0300
Warning Group 1, memory (Bckup Mem Status) is not redundant and operational with minimal resources
  1. Check the event logs for other memory errors that might occur (see Event logs).
  2. Reseat all of the memory modules in the blade server (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
  3. Make sure all of the memory is enabled in the Setup utility (see Using the Setup utility). Notice which memory modules are disabled before you continue to the next step.
  4. Replace the memory modules that were disabled in the Setup utility (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
  5. (Trained service technician only) Replace the microprocessor that controls the failing memory module.
    Note: DIMM connectors 1 through 8 are controlled by the first microprocessor and DIMM connectors 9 through 16 are controlled by the second microprocessor.
    See Removing a microprocessor and heat sink and Installing a microprocessor and heat sink.
Error Code: 0x800B0500
Error Group 1, memory (Bckup Mem Status) is not redundant and not operational
  1. Check the event logs for other memory errors that might occur (see Event logs).
  2. Reseat all of the memory modules in the blade server (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
  3. Make sure all of the memory is enabled in the Setup utility (see Using the Setup utility). Notice which memory modules are disabled before you continue to the next step.
  4. Replace the memory modules that were disabled in the Setup utility (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
  5. (Trained service technician only) Replace the microprocessor that controls the failing memory module.
    Note: DIMM connectors 1 through 8 are controlled by the first microprocessor and DIMM connectors 9 through 16 are controlled by the second microprocessor.
    See Removing a microprocessor and heat sink and Installing a microprocessor and heat sink.
Error Code: 0x806F0007
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error Group 4, processor (One of CPUs) internal error
  1. Remove the blade server and ensure the processors are installed correctly (see Installing a microprocessor and heat sink).
  2. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  3. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
  4. (Trained service technician only) Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
  5. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Group 4, processor (All CPUs) internal error
  1. Remove the blade server and ensure the processors are installed correctly (see Installing a microprocessor and heat sink).
  2. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  3. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
  4. (Trained service technician only) Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
  5. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Processor X (CPU X Status) internal error [Note X=1,2]
  1. Remove the blade server and ensure the processors are installed correctly (see Installing a microprocessor and heat sink).
  2. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  3. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
  4. (Trained service technician only) Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
  5. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Code: 0x806F0009
Information System board (Host Power) power on/off Information only; no action is required.
Error Code: 0x806F000D
Information Hard drive X (SSD Exp Drive X) removed/installed [Note X=1,2] Information only; no action is required.
Error Code: 0x806F000F
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error FW/BIOS, firmware progress (Firmware Error) FW/BIOS ROM corruption

Install the latest UEFI firmware (see Updating firmware and device drivers).

Error FW/BIOS, firmware progress (Firmware Error) no system memory
  1. Make sure that the server contains the correct number of DIMMs of the correct DIMM type, in the correct order (see Installing a DIMM - BladeCenter HX5 for the correct order to install DIMMs).
  2. Reseat the DIMMs (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
  3. Install DIMMs in the correct order (see Installing a DIMM - BladeCenter HX5).
  4. Replace any DIMMs not of the same type as the other DIMMs installed (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5). For information about supported DIMM types, see thehttp://www.ibm.com/ servers/eserver/serverproven/compat/us/.
  5. Replace any failed DIMMs (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
  6. Restart the blade server four times, using either the power button on the front of the blade server or the advanced management module web interface.
  7. Remove the battery and reinstall the battery to clear CMOS memory and NVRAM. The real time clock will also be reset. See Removing the battery and Installing the battery.
Error FW/BIOS, firmware progress (Firmware Error) no usable system memory
  1. Make sure that the server contains the correct number of DIMMs, in the correct order (see Installing a DIMM - BladeCenter HX5).
  2. Reseat the DIMMs (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
  3. Install DIMMs in the correct order (see Installing a DIMM - BladeCenter HX5).
  4. Restart the blade server four times, using either the power button on the front of the blade server or the advanced management module web interface.
  5. Remove the battery and reinstall the battery to clear CMOS memory and NVRAM. The real time clock will also be reset.
Error FW/BIOS, firmware progress (ABR Status) FW/BIOS ROM corruption
  1. Run the Setup utility (see Using the Setup utility). Select Load Default Settings and save the settings. to recover the server firmware.
  2. Reseat the blade server in the BladeCenter chassis (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
Error Code: 0x806F0013
Error Chassis (NMI State) diagnostic interrupt
  1. Verify that the latest system firmware is installed (see Updating firmware and device drivers).
  2. If an expansion card is installed in the blade server, verify that the firmware for each expansion card is up to date.
  3. Run the Setup utility and restore system setting to defaults (see Using the Setup utility).
  4. Check the event logs for other related error messages (see Event logs).
  5. Remove each expansion card, one at a time until the error does not occur (see Removing an I/O expansion card).
  6. Replace failing adapter and reinstall any other expansion cards that were removed (see Installing an I/O expansion card).
  7. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Code: 0x806F0021
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error PCI express bus 1 connector (CFFh Exp) fault
  1. Verify that the latest system firmware is installed (see Updating firmware and device drivers).
  2. Verify that the firmware for the CFFh expansion card is up to date.
  3. Run the Setup utility and restore system setting to defaults (see Using the Setup utility).
  4. Check the event logs for other related error messages (see Event logs).
  5. Reseat the CFFh expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
  6. Replace the CFFh expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
  7. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error PCI express bus 2 connector (CIOh Exp 2 ) fault
  1. Verify that the latest system firmware is installed (see Updating firmware and device drivers).
  2. Verify that the firmware for the CIOh expansion card is up to date.
  3. Run the Setup utility and restore system setting to defaults (see Using the Setup utility).
  4. Check the event logs for other related error messages (see Event logs).
  5. Reseat the CIOh expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
  6. Replace the CIOh expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
  7. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error PCI express bus 3 connector (CIOv Exp) fault
  1. Verify that the latest system firmware is installed (see Updating firmware and device drivers).
  2. Verify that the firmware for the CIOv expansion card is up to date.
  3. Run the Setup utility and restore system setting to defaults (see Using the Setup utility).
  4. Check the event logs for other related error messages (see Event logs).
  5. Reseat the CIOv expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
  6. Replace the CIOv expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
  7. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Code: 0x806F0029
Information PCI express bus 3, battery (SAS DC Batt) low

Information only; no action is required.

Error Code: 0x806F002B
Information System mgmt software (Scale Config) hardware change detected
Information only; no action is required.
Note: This event is not displayed in the advanced management module event log. However, it is sent for alerts and SNMP traps.
Error Code: 0x806F0107
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error Group 4, processor (One of CPUs) thermal trip
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all of the fans on the BladeCenter chassis are running.
  4. Make sure that each bay of the BladeCenter chassis contains either a device or a filler.
  5. Make sure that the blade server is not missing any heat sinks, DIMMs, or heat-sink fillers (see Parts listing - BladeCenter HX5).
  6. (Trained service technician only) Make sure that the microprocessor heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
  7. (Trained service technician only) Replace the microprocessor. See Removing a microprocessor and heat sink and Installing a microprocessor and heat sink.
Error Group 4, processor (ALL CPUs) thermal trip
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all of the fans on the BladeCenter chassis are running.
  4. Make sure that each bay of the BladeCenter chassis contains either a device or a filler.
  5. Make sure that the blade server is not missing any heat sinks, DIMMs, or heat-sink fillers (see Parts listing - BladeCenter HX5).
  6. (Trained service technician only) Make sure that the microprocessor heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
  7. (Trained service technician only) Replace the microprocessor. See Removing a microprocessor and heat sink and Installing a microprocessor and heat sink.
Error Processor X (CPU X Status) thermal trip [Note: X=1-2]
  1. Make sure that the room temperature is within the operating specifications (see Features and specifications).
  2. Make sure that none of the air vents on the BladeCenter chassis and on the blade server are blocked.
  3. Make sure that all of the fans on the BladeCenter chassis are running.
  4. Make sure that each bay of the BladeCenter chassis contains either a device or a filler.
  5. Make sure that the blade server is not missing any heat sinks, DIMMs, or heat-sink fillers (see Parts listing - BladeCenter HX5).
  6. (Trained service technician only) Make sure that the microprocessor heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
  7. (Trained service technician only) Replace the microprocessor. See Removing a microprocessor and heat sink and Installing a microprocessor and heat sink.
Error Code: 0x806F010C
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error Group 1, memory (One of the DIMMs) uncorrectable ECC memory error
  1. Refer to TIP H21455 for minimum code level.
  2. Check the IBM support website for an applicable retain tip or firmware update that applies to this memory error.
  3. Swap one of the DIMMs with a DIMM of the same size and type from another channel (see Installing a DIMM - BladeCenter HX5. For example, if a problem occurs on DIMM 1 and DIMM 4, swap DIMM 1 with a similar DIMM in slot 9.
  4. Enable all affected DIMMs using the Setup utility.
  5. If the failure remains on the original DIMM slots, replace the DIMM that was not moved. If the failure follows the DIMM that was moved, replace the DIMM that was swapped.
  6. If the problem occurs on the same DIMM connector, check the DIMM connector. If the connector is damaged, (Trained service technician only) replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Memory device X (DIMM X Status) uncorrectable ECC memory error [Note: X=1-16]
  1. Check the IBM support website for an applicable retain tip or firmware update that applies to this memory error.
  2. Swap one of the DIMMs with a DIMM of the same size and type from another channel (see Installing a DIMM - BladeCenter HX5. For example, if a problem occurs on DIMM 1 and DIMM 4, swap DIMM 1 with a similar DIMM in slot 9.
  3. Enable all affected DIMMs using the Setup utility.
  4. If the failure remains on the original DIMM slots, replace the DIMM that was not moved. If the failure follows the DIMM that was moved, replace the DIMM that was swapped.
  5. If the problem occurs on the same DIMM connector, check the DIMM connector. If the connector is damaged, (Trained service technician only) replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Memory device X (MEU DIMM X Status) uncorrectable ECC memory error [Note: X=1-24]
  1. Check the IBM support website for an applicable retain tip or firmware update that applies to this memory error.
  2. Swap one of the DIMMs with a DIMM of the same size and type from another channel (see Installing a DIMM - IBM MAX5.
  3. Enable all affected DIMMs using the Setup utility.
  4. If the failure remains on the original DIMM slots, replace the DIMM that was not moved. If the failure follows the DIMM that was moved, replace the DIMM that was swapped.
  5. If the problem occurs on the same DIMM connector, check the DIMM connector. If the connector is damaged, (Trained service technician only) replace the system-board assembly (see Removing an IBM MAX5 expansion blade and Installing an IBM MAX5 expansion blade).
Error Code: 0x806F010D
Error Hard drive X (SSD Exp Drive X) fault Note: X=1-2 Replace the specified storage drive (see Removing a solid state drive and Installing a solid state drive).
Error Code: 0x806F010F
Error FW/BIOS, firmware progress (Firmware error) hang Attempt to reboot the blade server.
Error Code: 0x806F0112
Information Group 4, processor (CPU Fault Reboot) OEM system boot event Information only; no action is required.
Error Code: 0x806F0113
Error Chassis (NMI State) bus timeout
  1. Remove the blade server from the BladeCenter chassis; then, reinstall it.
  2. Reseat all the optional devices installed in the blade server one device at a time, restarting the blade server each time, to determine where the problem is located.
  3. Remove optional devices from the blade server one at a time to determine where the problem is located.
  4. Replace the following components one at a time, in the order shown, restarting the blade server each time:
    1. All optional devices installed in the blade server
    2. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Code: 0x806F011B
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error System board, interconnect (Scale-Flex cable) configuration error
  1. Reseat the scalable blade complex (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
  2. Reseat the scalability expansion card (see Removing the 2-node scalability card and Installing the 2-node Scalability card).
  3. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Blade bezel 1, interconnect (Front panel) configuration error
  1. Reseat the operator control panel (see Removing the control panel and Installing the control panel).
  2. Replace the operator control panel (see Removing the control panel and Installing the control panel).
Error Interconnect 5 (SideScale Card) configuration error
  1. Reseat the scalable blade complex (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
  2. Reseat the scalability expansion card (see Removing the 2-node scalability card and Installing the 2-node Scalability card, or Removing the 1-node speed burst card and Installing the 1-node speed burst card).
  3. Update the firmware for the blade server (see Updating firmware and device drivers).
  4. Replace the scalability expansion card (see Removing the 2-node scalability card and Installing the 2-node Scalability card, or Removing the 1-node speed burst card and Installing the 1-node speed burst card).
  5. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Interconnect 5 (Unknown Scale ID) configuration error
  1. Reseat the scalable blade complex (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
  2. Reseat the scalability expansion card (see Removing the 2-node scalability card and Installing the 2-node Scalability card, or Removing the 1-node speed burst card and Installing the 1-node speed burst card).
  3. Attempt to create the hardware partition again (see Working with a scalable blade complex).
  4. Update the firmware for the blade server (see Updating firmware and device drivers).
  5. Replace the scalability expansion card (see Removing the 2-node scalability card and Installing the 2-node Scalability card, or Removing the 1-node speed burst card and Installing the 1-node speed burst card).
  6. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Code: 0x806F012B
Information System mgmt software (Scale Config) software change detected
Information only; no action is required.
Note: This event is not be displayed in the advanced management module event log. However, it is sent for alerts and SNMP traps.
Error Code: 0x806F0129
Error PCI express bus 3, battery (SAS DC Batt) failed
  1. Reseat the battery for the storage interface card.
  2. Replace the battery for the storage interface card.
Error Code: 0x806F0207
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error Group 4, processor (One of CPUs) BIST failure
  1. Remove the blade server and ensure the processors are installed correctly (see Installing a microprocessor and heat sink).
  2. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  3. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
  4. (Trained service technician only) Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
  5. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Group 4, processor (all CPUs) BIST failure
  1. Remove the blade server and ensure the processors are installed correctly (see Installing a microprocessor and heat sink).
  2. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  3. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
  4. (Trained service technician only) Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
  5. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Processor X (CPU X Status) BIST failure [Note X=1,2]
  1. Remove the blade server and ensure the processors are installed correctly (see Installing a microprocessor and heat sink).
  2. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  3. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
  4. (Trained service technician only) Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
  5. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Code: 0x806F0208
Warning System board, Power Module (EPOW Fault) predictive failure This warning message generally indicates that power redundancy for the blade was lost. The non redundant condition may have subsequently transitioned back to redundant power state.
  1. Check to see if a power module has been removed or replaced and ensure the power modules are installed and functioning properly (see the Installation and User's Guide for your chassis).
  2. If this warning message is not a result of power redundancy state changes, and there are no other indications of chassis power issues, (trained service technician only) replace the system board assembly (see Removing an IBM MAX5 expansion blade and Installing an IBM MAX5 expansion blade).
Error Code: 0x806F020D
Warning Hard drive X (SSD Exp Drive X) predictive failure [Note: X=1,2] Replace the storage drive (see Removing a solid state drive and Installing a solid state drive).
Error Code: 0x806F0229
Information PCI express bus 3, battery (SAS DC Batt) absent.

Information only; no action is required.

Error Code: 0x806F030C
Error Memory device X (DIMM X Status) memory scrub failed [Note: X=1-16]
  1. Refer to TIP H21455 for minimum code level.
  2. Check the IBM support website for an applicable retain tip or firmware update that applies to this memory error.
  3. Swap the affected DIMMs (as indicated by the error LEDs on the system board or the event logs) to a different memory channel or microprocessor (see Installing a DIMM - BladeCenter HX5 for memory population sequence).
  4. Enable all affected DIMMs using the Setup utility.
  5. If the failure remains on the original DIMM slots, replace the DIMM that was not moved. If the failure follows the DIMM that was moved, replace the DIMM that was swapped.
  6. If the problem occurs on the same DIMM connector, check the DIMM connector. If the connector is damaged, (Trained service technician only) replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Code: 0x806F0313
Error Chassis (NMI State) software NMI A software nonmaskable interrupt (NMI) has been detected.
  1. Check the operating system event log for any related errors and resolve those errors. If you cannot resolve those errors, contact the appropriate service provider for the software.
  2. Check the application log for any related errors and resolve those errors. If you cannot resolve those errors, contact the applicable service provider for the software.
  3. Check the IBM Support web page for any service bulletins that might be related to this problem.
Error Code: 0x806F032B
Error System mgmt software (Scale Config) software incompatibility
  1. If this error is occurring on a blade server operating in stand-alone mode, update the FPGA firmware.
  2. If this error is occurring on a blade server that is part of a scalable blade complex operating in single partition mode, make sure that the firmware for all IMMs and Field Programmable Gate Arrays (FPGAs) are at the same level in the blade complex.
Error Code: 0x806F0409
Information System board (Host Power) AC lost
Information only; no action is required.
Note: This event isl not be displayed in the advanced management module event log. However, it is sent for alerts and SNMP traps.
Error Code: 0x806F040C
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Information Group 1, (One of the DIMMs) memory disabled
  1. Check the system event log for any memory errors that might be related to the specified DIMM and resolve those errors.
  2. Enable the DIMM connector for the specified DIMM using the Setup utility or the Advanced Settings Utility (ASU) (see Using the Setup utility or Using the Advanced Settings Utility (ASU)).
  3. Reseat the affected DIMM (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5) and enable the DIMM connector (see step 2).
  4. Save the settings and exit from the Setup utility.
Information Memory device X (DIMM X Status) memory disabled [Note X = 1-16]
  1. Check the system event log for any memory errors that might be related to the specified DIMM and resolve those errors.
  2. Enable the DIMM connector for the specified DIMM using the Setup utility or the Advanced Settings Utility (ASU) (see Using the Setup utility or Using the Advanced Settings Utility (ASU)).
  3. Reseat the affected DIMM (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5) and enable the DIMM connector (see step 2).
  4. Save the settings and exit from the Setup utility.
Information Memory device X (MEU DIMM X Status) memory disabled [Note X = 1-24]
  1. Check the system event log for any memory errors that might be related to the specified DIMM and resolve those errors.
  2. Enable the DIMM connector for the specified DIMM using the Setup utility or the Advanced Settings Utility (ASU) (see Using the Setup utility or Using the Advanced Settings Utility (ASU)).
  3. Reseat the affected DIMM (see Removing a DIMM - IBM MAX5 expansion blade and Installing a DIMM - IBM MAX5) and enable the DIMM connector (see step 2).
  4. Save the settings and exit from the Setup utility.
Error Code: 0x806F0413
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error Expansion Module X, (BPE4_Y Slot Z) PCI parity error
Note:
  1. X = Module number
  2. Y = BPE4 ID (1, 2, 3, or 4). The max BPE4 number is 4, and there are 2 slots in each BPE4. Module number is based on the configuration of the BPE4
  1. If you have a PCI adapter in your blade server, verify that the PCI adapter is supported in the blade server. For a list of supported optional devices for the blade server, see the http://www.ibm.com/servers/eserver/serverproven/compat/us/.
  2. Reseat the PCI adapter (see Removing an I/O expansion card and Installing an I/O expansion card).
Error Code: 0x806F0507
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error Group 4, processor (One of CPUs) configuration error
  1. (Trained service personnel only) Remove the blade server and reseat the processors (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
  2. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  3. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
Error Group 4, processor (4S CPU) configuration error
  1. (Trained service personnel only) Remove the blade server and reseat the processors (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
  2. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  3. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
Error Group 4, processor (2S CPU) configuration error
  1. (Trained service personnel only) Remove the blade server and reseat the processors (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
  2. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  3. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
Error Group 4, processor (All CPUs) configuration error
  1. (Trained service personnel only) Remove the blade server and reseat the processors (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
  2. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  3. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
Error Processor X (CPU X Status) configuration error [Note X=1,2]
  1. (Trained service personnel only) Remove the blade server and reseat the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
  2. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  3. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
Error Group 4, processor (Missing Boot CPU) configuration error
  1. (Trained service personnel only) Remove the blade server and reseat the processors (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
  2. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  3. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
Error Code: 0x806F050C
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error Group 1, memory (One of the DIMMs) correctable ECC memory error logging limit reached
  1. Refer to TIP H21455 for minimum code level.
  2. Check the IBM support website for an applicable retain tip or firmware update that applies to this memory error.
  3. Swap the affected DIMMs (as indicated by the error LEDs on the system board or the event logs) to a different memory channel or microprocessor (see Installing a DIMM - BladeCenter HX5 for memory population sequence).
  4. If the error still occurs on the same DIMM, replace the affected DIMM (as indicated by the error LEDs on the system board or the event logs).
  5. If the problem occurs on the same DIMM connector, check the DIMM connector. If the connector is damaged, (trained service technician only) replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Memory device X (DIMM X Status) correctable ECC memory error logging limit reached [Note X = 1-16]
  1. Check the IBM support website for an applicable retain tip or firmware update that applies to this memory error.
  2. Swap the affected DIMMs (as indicated by the error LEDs on the system board or the event logs) to a different memory channel or microprocessor (see Installing a DIMM - BladeCenter HX5 for memory population sequence).
  3. If the error still occurs on the same DIMM, replace the affected DIMM (as indicated by the error LEDs on the system board or the event logs).
  4. If the problem occurs on the same DIMM connector, check the DIMM connector. If the connector is damaged, (trained service technician only) replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Code: 0x806F050D
Error Hard drive X (SSD Exp Drive X) in critical array Note: X=1-2
  1. Replace the storage drive (see Removing a solid state drive and Installing a solid state drive).
  2. Rebuild the RAID array (see Using the LSI Logic Configuration Utility program).
Error Code: 0x806F0513
Error Expansion Module X, (BPE4_Y Slot Z) PCI system error
Note:
  1. X = Module number
  2. Y = BPE4 ID (1, 2, 3, or 4). The max BPE4 number is 4, and there are 2 slots in each BPE4. Module number is based on the configuration of the BPE4
  1. If you have a PCI adapter in your blade server, verify that the PCI adapter is supported in the blade server. For a list of supported optional devices for the blade server, see the http://www.ibm.com/servers/eserver/serverproven/compat/us/.
  2. Reseat the PCI adapter (see Removing an I/O expansion card and Installing an I/O expansion card).
Error Code: 0x806F052B
Error System mgmt software, (IMM FW Failover) unsupported software version

This error occurs when the service processor (IMM) firmware is corrupted and has reverted to a previous version of the firmware.

Complete the following steps to correct this error:
  1. Check the IBM support website for an applicable firmware update that applies to the blade server.
  2. Restart the IMM and verify the IMM is running the correct firmware level after the firmware update.

For more information about updating the firmware and the preferred methods, see Firmware Update Best Practices at http://www-947.ibm.com/support/entry/portal/docdisplay?brand=5000020&lndocid=MIGR-5082923.

Error Code: 0x806F0607
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error Group 4, processor (One of CPUs) SM BIOS uncorrectable error
  1. Verify that the latest system firmware is installed (see Updating firmware and device drivers).
  2. (Trained service technician only) Replace the microprocessors one at a time (see Removing a microprocessor and heat sink and Removing a microprocessor and heat sink).
  3. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Group 4, processor (all CPUs) SM BIOS uncorrectable error
  1. Verify that the latest system firmware is installed (see Updating firmware and device drivers).
  2. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Processor X (CPU X Status) SM BIOS uncorrectable error
  1. Verify that the latest system firmware is installed (see Updating firmware and device drivers).
  2. (Trained service technician only) Replace microprocessor X (see Removing a microprocessor and heat sink and Removing a microprocessor and heat sink).
  3. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Code: 0x806F060D
Error Hard drive X (SSD Exp Drive X) in failed array Note: X=1-2 This error occurs because one or more hard drives in the RAID array have a fault. Perform these steps:
  1. Check the event log for errors related to hard drive faults. See Event logs for more information.
  2. Replace the storage drive that has a fault (see Removing a solid state drive and Installing a solid state drive).
  3. Rebuild the RAID array (see Using the LSI Logic Configuration Utility program).
Error Code: 0x806F070C
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error Group 1, memory (All DIMMs) memory configuration error Make sure that the DIMMs are installed in the correct order and configured correctly (see Installing a DIMM - BladeCenter HX5).

If you receive this error code for a blade server configuration that includes an IBM MAX5 expansion blade, multiple DIMMs might have been disabled. After you replace the mismatched DIMM, make sure that all DIMMs have been enabled using the Setup utility (see Using the Setup utility) or using the Advanced Settings Utility (see Using the Advanced Settings Utility (ASU)).

Error Group 1, memory (One of the DIMMs) memory configuration error Make sure that the DIMMs are installed in the correct order and configured correctly (see Installing a DIMM - BladeCenter HX5).

If you receive this error code for a blade server configuration that includes an IBM MAX5 expansion blade, multiple DIMMs might have been disabled. After you replace the mismatched DIMM, make sure that all DIMMs have been enabled using the Setup utility (see Using the Setup utility) or using the Advanced Settings Utility (see Using the Advanced Settings Utility (ASU)).

Error Memory device X (DIMM X Status) memory configuration error [Note X=1-16] Make sure that the DIMMs are installed in the correct order and configured correctly (see Installing a DIMM - BladeCenter HX5).

If you receive this error code for a blade server configuration that includes an IBM MAX5 expansion blade, multiple DIMMs might have been disabled. After you replace the mismatched DIMM, make sure that all DIMMs have been enabled using the Setup utility (see Using the Setup utility) or using the Advanced Settings Utility (see Using the Advanced Settings Utility (ASU)).

Error Memory device X (MEU DIMM X Status) memory configuration error [Note X=1-24] Make sure that the DIMMs are installed in the correct order and configured correctly (see Installing a DIMM - IBM MAX5).

If you receive this error code for a blade server configuration that includes an IBM MAX5 expansion blade, multiple DIMMs might have been disabled. After you replace the mismatched DIMM, make sure that all DIMMs have been enabled using the Setup utility (see Using the Setup utility) or using the Advanced Settings Utility (see Using the Advanced Settings Utility (ASU)).

Error Code: 0x806F070D
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Information Hard drive X (SSD Exp Drive X) rebuild in progress Information only; no action is required.
Information Hard drive X (SSD Exp Drive X) rebuild complete Information only; no action is required.
Error Code: 0x806F0807
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Information Group 4, processor (One of CPUs) disabled
  1. Check the event logs for other related error messages (see Event logs).
  2. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  3. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
  4. (Trained service technician) Remove the blade server and ensure the processors are installed correctly (see Installing a microprocessor and heat sink).
Information Group 4, processor (All CPUs) disabled
  1. Check the event logs for other related error messages (see Event logs).
  2. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  3. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
  4. (Trained service technician) Remove the blade server and ensure the processors are installed correctly (see Installing a microprocessor and heat sink).
Information Processor X (CPU X Status) disabled [Note X=1,2]
  1. Check the event logs for other related error messages (see Event logs).
  2. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  3. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
  4. (Trained service technician) Remove the blade server and ensure the processors are installed correctly (see Installing a microprocessor and heat sink).
Error Code: 0x806F0813
Note: Multiple events can be displayed for this error code. Be sure to read the message text to determine the appropriate recovery actions.
Error Expansion Module X, (BPE4_Y Slot Z) bus uncorrectable error
Note:
  1. X = Module number
  2. Y = BPE4 ID (1, 2, 3, or 4). The max BPE4 number is 4, and there are 2 slots in each BPE4. Module number is based on the configuration of the BPE4
  1. Update the firmware for the service processor (BMC), BIOS, and firmware for the advanced management module.
  2. Reseat the memory DIMMs and any expansion cards (see Removing and replacing Tier 1 customer replaceable units (CRUs)).
  3. (Trained service technician only) Replace the system board (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Group 4, processor (Critical Int CPU) bus uncorrectable error
  1. Remove the blade server and ensure the processors are installed correctly (see Installing a microprocessor and heat sink).
  2. Check the event logs for other related error messages (see Event logs).
  3. Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
  4. Run the Setup utility (see Using the Setup utility).
    1. Make sure that both processors are displayed by the system.
    2. Load the default settings.
    3. Go to the System Settings menu and make sure the processor is enabled.
Error PCI express bus 0 (Planar PCIe Err) bus uncorrectable error
  1. Reseat the blade server (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
  2. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Group 1, memory (Critical Int DIM) bus uncorrectable error
  1. Check the event logs for other memory errors that might occur (see Event logs).
  2. Reseat all of the memory modules in the blade server (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
  3. Make sure all of the memory is enabled in the Setup utility (see Using the Setup utility). Notice which memory modules are disabled before you continue to the next step.
  4. Replace the memory modules that were disabled in the Setup utility (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
  5. (Trained service technician only) Replace the microprocessor that controls the failing memory module.
    Note: DIMM connectors 1 through 8 are controlled by the first microprocessor and DIMM connectors 9 through 16 are controlled by the second microprocessor.
    See Removing a microprocessor and heat sink and Installing a microprocessor and heat sink.
  6. (Trained service technician only) Replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
Error Sub-chassis 1, (Critical Int EXA) bus uncorrectable error
  1. Check the IBM MAX5 expansion blade for any lit error LEDs.
  2. Reseat the IBM MAX5 expansion blade (see Removing an IBM MAX5 expansion blade and Installing an IBM MAX5 expansion blade).
  3. If the error still occurs, replace the IBM MAX5 expansion blade (see Removing an IBM MAX5 expansion blade and Installing an IBM MAX5 expansion blade).