Error Code: 0x80010200 Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
System board (Planar 12V) voltage under critical
threshold. Reading: X, Threshold: Y |
- If the under voltage problem is occurring on all blade servers,
look for other events in the log related to power and resolve those
events (see Event logs).
- View the event log provided by the advanced management module
for your BladeCenter chassis and resolve any power related errors
that might be displayed.
- If other modules or blade servers are logging the same issue,
check the power supply for the BladeCenter chassis.
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
System board (Planar 5V) voltage under critical
threshold. Reading: X, Threshold: Y |
- Remove all expansion cards from the blade server (see Removing an I/O expansion card).
- Remove all storage drives from the blade server (see Removing a solid state drive).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
System board (Planar 3.3V) voltage under critical
threshold. Reading: X, Threshold: Y |
- Remove all expansion cards from the blade server (see Removing an I/O expansion card).
- Remove all storage drives from the blade server (see Removing a solid state drive).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error Code: 0x80010201 |
Error |
CMOS Battery (CMOS Battery) voltage under critical
threshold. Reading: X, Threshold: Y |
Replace the system battery (see Removing the battery and Installing the battery). |
Error Code: 0x80010900 Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
System board (Planar 12V) voltage over critical
threshold. Reading: X, Threshold: Y |
- If the over voltage problem is occurring on all blade servers,
look for other events in the log related to power and resolve those
events.
- View the event log provided by the advanced management module
for your BladeCenter chassis and resolve any power-related errors
that might be displayed.
- If other modules or blade servers are logging the same issue,
check the power supply for the BladeCenter chassis.
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
System board (Planar 5V) voltage over critical
threshold. Reading: X, Threshold: Y |
- Remove all expansion cards from the blade server (see Removing an I/O expansion card).
- Remove all storage drives from the blade server (see Removing a solid state drive).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
System board (Planar 3.3V) voltage over critical
threshold. Reading: X, Threshold: Y |
(Trained service technician only) Replace the
system board (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5). |
Error Code: 0x80030100 |
Information |
Group 1, memory (Mem Lane Spared) occurred/recovered. |
Information only.
|
Error Code: 0x80070100 Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Warning |
Expansion Module X, (BPE4_Y Slot Z) bus uncorrectable errorNote:
- X = Module number
- Y = BPE4 ID (1, 2, 3, or 4). The max BPE4 number is 4,
and there are 2 slots in each BPE4. Module number is based on the
configuration of the BPE4
|
- Update the firmware for the service processor (BMC), BIOS, and
firmware for the advanced management module.
- Reseat the memory DIMMs (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
- Reseat any expansion cards that are installed (see Removing an I/O expansion card and Installing an I/O expansion card).
- (Trained service technician only) Replace the system board (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Warning |
Group 2, (PCI express bus X, Expansion
Module Y) firmware progress (I/O Resources) warning Note:
- X = PCI slot (1, 2, or 3)
- Y = Module number (0, 1, or 2)
|
To allow more PCIe space, choose one of the
following steps:
- Change MM configuration setting to 1 GB.
- In the Setup utility, click .
- Set to 1 GB.
- Enable PCI 64-bit resource.
- In the Setup utility, click .
- Enable .
|
Warning |
Processor X, temperature (CPU X OverTemp) warning [Note: X=1-2] |
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all of the fans on the BladeCenter chassis are
running.
|
Warning |
System board, temperature (Inlet Temp) warning |
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all of the fans on the BladeCenter chassis are
running.
|
Warning |
System board, temperature (MEU Overtemp) warning |
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all of the fans on the BladeCenter chassis are
running.
|
Warning |
Memory device X, temperature (DIMM X) warning [Note: X=1-16] |
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all of the fans on the BladeCenter chassis are
running.
|
Warning |
Memory deviceX, temperature (MEU DIMM X) warning [Note: X=1-24] |
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all of the fans on the BladeCenter chassis are
running.
|
Error Code: 0x80070200 Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
Chassis, processor (CPU Cooling) critical |
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all the fans are on the BladeCenter chassis are
running (see the documentation for your BladeCenter chassis).
- Make sure Acoustics mode is not enabled on the BladeCenter chassis
(see the documentation for your BladeCenter chassis).
- (Trained service technician only) Make sure that the microprocessor
heat sink is properly attached to the CPU (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
- Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
|
Error |
Expansion Module X, Expansion Card (BPE4_Y Fault) criticalNote:
- X = Module number
- Y = BPE4 ID (1, 2, 3, or 4). The max BPE4 number is 4,
and there are 2 slots in each BPE4. Module number is based on the
configuration of the BPE4
|
- Reseat the blade expansion unit (see Removing an expansion unit and Installing an expansion unit).
- Replace the blade expansion unit (see Removing an expansion unit and Installing an expansion unit).
|
Error |
Processor X, temperature (CPU X OverTemp) critical [Note: X=1-2] |
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all of the fans on the BladeCenter chassis are
running.
- (Trained service technician only) Make sure that the microprocessor
heat sink is properly attached to the CPU (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
- (Trained service technician only) Replace the processor
(see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
|
Error |
Memory device X, temperature (DIMM X Temp) critical [Note:X=1-16] |
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all of the fans on the BladeCenter chassis are
running.
- (Trained service technician only) Make sure that the microprocessor
heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
|
Error |
Memory device X, temperature (MEU DIMM X Temp) critical [Note:X=1-24] |
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all of the fans on the BladeCenter chassis are
running.
- (Trained service technician only) Make sure that the microprocessor
heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
|
Error |
Group 1 (mem dev 1-40) memory (MEU Mem Lane)
critical |
- Reseat the IBM MAX5 expansion blade (see Removing an IBM MAX5 expansion blade and Installing an IBM MAX5 expansion blade).
- Replace the IBM MAX5 expansion blade (see Removing an IBM MAX5 expansion blade and Installing an IBM MAX5 expansion blade).
|
Error |
System board, voltage (Planar Fault) critical |
- Reseat the blade server in the BladeCenter chassis (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
- Remove the blade server from the BladeCenter chassis and install
an identical known good blade server in the BladeCenter chassis (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis). If the problem is related to a power supply, replace the power
supply.
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
System board, temperature (Inlet Temp) critical |
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all of the fans on the BladeCenter chassis are
running.
|
Error |
Proc/IO module 1, temperature (IOH Temp) critical |
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all of the fans on the BladeCenter chassis are
running.
|
Error |
System board, chip set (Sys Board Fault) critical |
- Make sure that the latest firmware is being used (see Updating firmware and device drivers).
- Reset the UEFI firmware settings to default values using the Setup
utility (see Using the Setup utility).
- Reseat the blade server in the BladeCenter chassis (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
Processor X, interconnect (CPU X Int Link) critical [Note: X=1-2] |
- Remove the blade server and ensure the processors are installed
correctly (see Installing a microprocessor and heat sink).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Verify that the scalability card is installed correctly (see Removing the 2-node scalability card and Installing the 2-node Scalability card, or see Removing the 1-node speed burst card and Installing the 1-node speed burst card).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
- (Trained service technician only) Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
- Replace the scalability card (see Removing the 2-node scalability card and Installing the 2-node Scalability card, or see Removing the 1-node speed burst card and Installing the 1-node speed burst card).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
Interconnect X, connector (Ext QPI Link X) critical [Note: X=1-4] |
- Remove the blade server and ensure the processors are installed
correctly (see Installing a microprocessor and heat sink).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Verify that the scalability card is installed correctly (see Removing the 2-node scalability card and Installing the 2-node Scalability card, or see Removing the 1-node speed burst card and Installing the 1-node speed burst card).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
- (Trained service technician only) Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
- Replace the scalability card (see Removing the 2-node scalability card and Installing the 2-node Scalability card, or see Removing the 1-node speed burst card and Installing the 1-node speed burst card).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
PCI express bus 1, Expansion Card (CFFh Exp)
critical |
- Check the operating-system event log and the system-event log
because it might contain additional information (see Event logs).
- Update the device drivers for the CFFh expansion card.
- Reseat the blade server in the BladeCenter chassis (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
- Reseat the expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
- Replace the expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
|
Error |
PCI express bus 2, Expansion Card (CIOh Exp
2 Fault) critical |
- Check the operating-system event log and the system-event log
because it might contain additional information (see Event logs).
- Update the device drivers for the CIOh expansion card.
- Reseat the blade server in the BladeCenter chassis (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
- Reseat the expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
- Replace the expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
|
Error |
PCI express bus 3, Expansion Card (CIOv Exp
Fault) critical |
- Check the operating-system event log and the system-event log
because it might contain additional information (see Event logs).
- Update the device drivers for the CIOv expansion card.
- Reseat the blade server in the BladeCenter chassis (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
- Reseat the expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
- Replace the expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
|
Error Code: 0x80070300 Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
Expansion Module X, temperature (BPE4_Y TMP) non-recoverableNote:
- X = Module number
- Y = BPE4 ID (1, 2, 3, or 4). The max BPE4 number is 4,
and there are 2 slots in each BPE4. Module number is based on the
configuration of the BPE4
|
- Check the room ambient temperature to ensure that it is within
the operating specifications for the chassis (see Features and specifications).
- If an air filter is installed, make sure that it is cleaned or
replaced (see the documentation for your BladeCenter chassis).
- Make sure that all fan/blower modules are running. Replace fan
modules if necessary (see the documentation for your BladeCenter chassis).
- Make sure that a device or filler is installed in each bay in
the front and rear of the chassis, and make sure that there is nothing
covering the bays. Any missing components can cause a major reduction
in airflow for the blade server (see the documentation for your BladeCenter
chassis).
|
|
Expansion Module X, voltage (BPE4_Y VOL) non-recoverableNote:
- X = Module number
- Y = BPE4 ID (1, 2, 3, or 4). The max BPE4 number is 4,
and there are 2 slots in each BPE4. Module number is based on the
configuration of the BPE4
|
- Check the room ambient temperature to ensure that it is within
the operating specifications for the chassis (see Features and specifications).
- If an air filter is installed, make sure that it is cleaned or
replaced (see the documentation for your BladeCenter chassis).
- Make sure that all fan/blower modules are running. Replace fan
modules if necessary (see the documentation for your BladeCenter chassis).
- Make sure that a device or filler is installed in each bay in
the front and rear of the chassis, and make sure that there is nothing
covering the bays. Any missing components can cause a major reduction
in airflow for the blade server (see the documentation for your BladeCenter
chassis).
|
Error |
Processor X, temperature (CPU X OverTemp) non-recoverable [Note: X=1-2] |
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all of the fans on the BladeCenter chassis are
running.
- Make sure that each bay of the BladeCenter chassis contains either
a device or a filler.
- Make sure that the blade server is not missing any heat sinks,
DIMMs, or heat-sink fillers (see Parts listing - BladeCenter HX5).
- (Trained service technician only) Make sure that the microprocessor
heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
|
Error |
System board, temperature (Inlet Temp) non-recoverable
|
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all of the fans on the BladeCenter chassis are
running.
- Make sure that each bay of the BladeCenter chassis contains either
a device or a filler.
- Make sure that the blade server is not missing any heat sinks,
DIMMs, or heat-sink fillers (see Parts listing - BladeCenter HX5).
- (Trained service technician only) Make sure that the microprocessor
heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
|
Error |
Proc/IO module 1, temperature (IOH Temp) non-recoverable |
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all of the fans on the BladeCenter chassis are
running.
- Make sure that each bay of the BladeCenter chassis contains either
a device or a filler.
- Make sure that the blade server is not missing any heat sinks,
DIMMs, or heat-sink fillers (see Parts listing - BladeCenter HX5).
- (Trained service technician only) Make sure that the microprocessor
heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
|
Error Code: 0x80070600 Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
Processor X, temperature (CPU X OverTemp) non-recoverable [Note: X=1-2] |
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all of the fans on the BladeCenter chassis are
running.
- Make sure that each bay of the BladeCenter chassis contains either
a device or a filler.
- Make sure that the blade server is not missing any heat sinks,
DIMMs, or heat-sink fillers (see Parts listing - BladeCenter HX5).
- (Trained service technician only) Make sure that the microprocessor
heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
|
Error |
System board, interconnect (Pwr Share Jumper)
non-recoverable |
- Reseat the cap on the power sharing connector (see Blade server connectors - BladeCenter HX5).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error Code: 0x80090000 |
Information |
System board, memory (Performance Mode) disabled/enabled |
This is informational only, no action is required.
The performance mode has been enabled or disabled. |
Error Code: 0x800B0100 |
Error |
Group 1, memory (Bckup Mem Status) is not redundant |
- Check the event logs for other memory errors that might occur
(see Event logs).
- Reseat all of the memory modules in the blade server (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
- Make sure all of the memory is enabled in the Setup utility (see Using the Setup utility). Notice which memory modules
are disabled before you continue to the next step.
- Replace the memory modules that were disabled in the Setup utility
(see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
- (Trained service technician only) Replace the microprocessor that
controls the failing memory module.
Note: DIMM connectors 1 through
8 are controlled by the first microprocessor and DIMM connectors 9
through 16 are controlled by the second microprocessor.
See Removing a microprocessor and heat sink and Installing a microprocessor and heat sink.
|
Error Code: 0x800B0300 |
Warning |
Group 1, memory (Bckup Mem Status) is not redundant
and operational with minimal resources |
- Check the event logs for other memory errors that might occur
(see Event logs).
- Reseat all of the memory modules in the blade server (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
- Make sure all of the memory is enabled in the Setup utility (see Using the Setup utility). Notice which memory modules
are disabled before you continue to the next step.
- Replace the memory modules that were disabled in the Setup utility
(see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
- (Trained service technician only) Replace the microprocessor that
controls the failing memory module.
Note: DIMM connectors 1 through
8 are controlled by the first microprocessor and DIMM connectors 9
through 16 are controlled by the second microprocessor.
See Removing a microprocessor and heat sink and Installing a microprocessor and heat sink.
|
Error Code: 0x800B0500 |
Error |
Group 1, memory (Bckup Mem Status) is not redundant
and not operational |
- Check the event logs for other memory errors that might occur
(see Event logs).
- Reseat all of the memory modules in the blade server (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
- Make sure all of the memory is enabled in the Setup utility (see Using the Setup utility). Notice which memory modules
are disabled before you continue to the next step.
- Replace the memory modules that were disabled in the Setup utility
(see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
- (Trained service technician only) Replace the microprocessor that
controls the failing memory module.
Note: DIMM connectors 1 through
8 are controlled by the first microprocessor and DIMM connectors 9
through 16 are controlled by the second microprocessor.
See Removing a microprocessor and heat sink and Installing a microprocessor and heat sink.
|
Error Code: 0x806F0007 Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
Group 4, processor (One of CPUs) internal error |
- Remove the blade server and ensure the processors are installed
correctly (see Installing a microprocessor and heat sink).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
- (Trained service technician only) Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
Group 4, processor (All CPUs) internal error |
- Remove the blade server and ensure the processors are installed
correctly (see Installing a microprocessor and heat sink).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
- (Trained service technician only) Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
Processor X (CPU X Status) internal
error [Note X=1,2] |
- Remove the blade server and ensure the processors are installed
correctly (see Installing a microprocessor and heat sink).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
- (Trained service technician only) Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error Code: 0x806F0009 |
Information |
System board (Host Power) power on/off |
Information only; no action is required. |
Error Code: 0x806F000D |
Information |
Hard drive X (SSD Exp Drive X)
removed/installed [Note X=1,2] |
Information only; no action is required. |
Error Code: 0x806F000F Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
FW/BIOS, firmware progress (Firmware Error)
FW/BIOS ROM corruption |
Install the latest UEFI firmware (see Updating firmware and device drivers).
|
Error |
FW/BIOS, firmware progress (Firmware Error)
no system memory |
- Make sure that the server contains the correct number of DIMMs
of the correct DIMM type, in the correct order (see Installing a DIMM - BladeCenter HX5 for the correct
order to install DIMMs).
- Reseat the DIMMs (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
- Install DIMMs in the correct order (see Installing a DIMM - BladeCenter HX5).
- Replace any DIMMs not of the same type as the other DIMMs installed
(see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5). For information
about supported DIMM types, see thehttp://www.ibm.com/
servers/eserver/serverproven/compat/us/.
- Replace any failed DIMMs (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
- Restart the blade server four times, using either
the power button on the front of the blade server or the advanced
management module web interface.
- Remove the battery and reinstall the battery to
clear CMOS memory and NVRAM. The real time clock will also be reset.
See Removing the battery and Installing the battery.
|
Error |
FW/BIOS, firmware progress (Firmware Error)
no usable system memory |
- Make sure that the server contains the correct number of DIMMs,
in the correct order (see Installing a DIMM - BladeCenter HX5).
- Reseat the DIMMs (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
- Install DIMMs in the correct order (see Installing a DIMM - BladeCenter HX5).
- Restart the blade server four times, using either
the power button on the front of the blade server or the advanced
management module web interface.
- Remove the battery and reinstall the battery to
clear CMOS memory and NVRAM. The real time clock will also be reset.
|
Error |
FW/BIOS, firmware progress (ABR Status) FW/BIOS
ROM corruption |
- Run the Setup utility (see Using the Setup utility). Select Load Default Settings and save the settings. to recover the server firmware.
- Reseat the blade server in the BladeCenter chassis (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
|
Error Code: 0x806F0013 |
Error |
Chassis (NMI State) diagnostic interrupt |
- Verify that the latest system firmware is installed (see Updating firmware and device drivers).
- If an expansion card is installed in the blade server, verify
that the firmware for each expansion card is up to date.
- Run the Setup utility and restore system setting to defaults (see Using the Setup utility).
- Check the event logs for other related error messages (see Event logs).
- Remove each expansion card, one at a time until the error does
not occur (see Removing an I/O expansion card).
- Replace failing adapter and reinstall any other expansion cards
that were removed (see Installing an I/O expansion card).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error Code: 0x806F0021 Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
PCI express bus 1 connector (CFFh Exp) fault |
- Verify that the latest system firmware is installed (see Updating firmware and device drivers).
- Verify that the firmware for the CFFh expansion card is up to
date.
- Run the Setup utility and restore system setting to defaults (see Using the Setup utility).
- Check the event logs for other related error messages (see Event logs).
- Reseat the CFFh expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
- Replace the CFFh expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
PCI express bus 2 connector (CIOh Exp 2 ) fault |
- Verify that the latest system firmware is installed (see Updating firmware and device drivers).
- Verify that the firmware for the CIOh expansion card is up to
date.
- Run the Setup utility and restore system setting to defaults (see Using the Setup utility).
- Check the event logs for other related error messages (see Event logs).
- Reseat the CIOh expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
- Replace the CIOh expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
PCI express bus 3 connector (CIOv Exp) fault |
- Verify that the latest system firmware is installed (see Updating firmware and device drivers).
- Verify that the firmware for the CIOv expansion card is up to
date.
- Run the Setup utility and restore system setting to defaults (see Using the Setup utility).
- Check the event logs for other related error messages (see Event logs).
- Reseat the CIOv expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
- Replace the CIOv expansion card (see Removing an I/O expansion card and Installing an I/O expansion card).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error Code: 0x806F0029 |
Information |
PCI express bus 3, battery (SAS DC Batt) low |
Information only; no action
is required.
|
Error Code: 0x806F002B |
Information |
System mgmt software (Scale Config) hardware
change detected |
Information only; no action
is required. Note: This event is not displayed in the advanced management
module event log. However, it is sent for alerts and SNMP traps.
|
Error Code: 0x806F0107 Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
Group 4, processor (One of CPUs) thermal trip |
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all of the fans on the BladeCenter chassis are
running.
- Make sure that each bay of the BladeCenter chassis contains either
a device or a filler.
- Make sure that the blade server is not missing any heat sinks,
DIMMs, or heat-sink fillers (see Parts listing - BladeCenter HX5).
- (Trained service technician only) Make sure that the microprocessor
heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
- (Trained service technician only) Replace the microprocessor.
See Removing a microprocessor and heat sink and Installing a microprocessor and heat sink.
|
Error |
Group 4, processor (ALL CPUs) thermal trip |
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all of the fans on the BladeCenter chassis are
running.
- Make sure that each bay of the BladeCenter chassis contains either
a device or a filler.
- Make sure that the blade server is not missing any heat sinks,
DIMMs, or heat-sink fillers (see Parts listing - BladeCenter HX5).
- (Trained service technician only) Make sure that the microprocessor
heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
- (Trained service technician only) Replace the microprocessor.
See Removing a microprocessor and heat sink and Installing a microprocessor and heat sink.
|
Error |
Processor X (CPU X Status) thermal
trip [Note: X=1-2] |
- Make sure that the room temperature is within the operating specifications
(see Features and specifications).
- Make sure that none of the air vents on the BladeCenter chassis
and on the blade server are blocked.
- Make sure that all of the fans on the BladeCenter chassis are
running.
- Make sure that each bay of the BladeCenter chassis contains either
a device or a filler.
- Make sure that the blade server is not missing any heat sinks,
DIMMs, or heat-sink fillers (see Parts listing - BladeCenter HX5).
- (Trained service technician only) Make sure that the microprocessor
heat sink is properly attached to the microprocessor (see Installing a microprocessor and heat sink).
- (Trained service technician only) Replace the microprocessor.
See Removing a microprocessor and heat sink and Installing a microprocessor and heat sink.
|
Error Code: 0x806F010C Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
Group 1, memory (One of the DIMMs) uncorrectable
ECC memory error |
- Refer to TIP H21455 for minimum code level.
- Check the IBM support website for an applicable retain tip or
firmware update that applies to this memory error.
- Swap one of the DIMMs with a DIMM of the same size and type from
another channel (see Installing a DIMM - BladeCenter HX5. For example,
if a problem occurs on DIMM 1 and DIMM 4, swap DIMM 1 with a similar
DIMM in slot 9.
- Enable all affected DIMMs using the Setup utility.
- If the failure remains on the original DIMM slots, replace the
DIMM that was not moved. If the failure follows the DIMM that was
moved, replace the DIMM that was swapped.
- If the problem occurs on the same DIMM connector, check the DIMM
connector. If the connector is damaged, (Trained service technician
only) replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
Memory device X (DIMM X Status)
uncorrectable ECC memory error [Note: X=1-16] |
- Check the IBM support website for an applicable retain tip or
firmware update that applies to this memory error.
- Swap one of the DIMMs with a DIMM of the same size and type from
another channel (see Installing a DIMM - BladeCenter HX5. For example,
if a problem occurs on DIMM 1 and DIMM 4, swap DIMM 1 with a similar
DIMM in slot 9.
- Enable all affected DIMMs using the Setup utility.
- If the failure remains on the original DIMM slots, replace the
DIMM that was not moved. If the failure follows the DIMM that was
moved, replace the DIMM that was swapped.
- If the problem occurs on the same DIMM connector, check the DIMM
connector. If the connector is damaged, (Trained service technician
only) replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
Memory device X (MEU DIMM X Status)
uncorrectable ECC memory error [Note: X=1-24] |
- Check the IBM support website for an applicable retain tip or
firmware update that applies to this memory error.
- Swap one of the DIMMs with a DIMM of the same size and type from
another channel (see Installing a DIMM - IBM MAX5.
- Enable all affected DIMMs using the Setup utility.
- If the failure remains on the original DIMM slots, replace the
DIMM that was not moved. If the failure follows the DIMM that was
moved, replace the DIMM that was swapped.
- If the problem occurs on the same DIMM connector, check the DIMM
connector. If the connector is damaged, (Trained service technician
only) replace the system-board assembly (see Removing an IBM MAX5 expansion blade and Installing an IBM MAX5 expansion blade).
|
Error Code: 0x806F010D |
Error |
Hard drive X (SSD Exp Drive X)
fault Note: X=1-2 |
Replace the specified storage drive (see Removing a solid state drive and Installing a solid state drive). |
Error Code: 0x806F010F |
Error |
FW/BIOS, firmware progress (Firmware error)
hang |
Attempt to reboot the blade server. |
Error Code: 0x806F0112 |
Information |
Group 4, processor (CPU Fault Reboot) OEM system
boot event |
Information only; no action is required. |
Error Code: 0x806F0113 |
Error |
Chassis (NMI State) bus timeout |
- Remove the blade server from the BladeCenter chassis; then, reinstall
it.
- Reseat all the optional devices installed in the blade server
one device at a time, restarting the blade server each time, to determine
where the problem is located.
- Remove optional devices from the blade server one at a time to
determine where the problem is located.
- Replace the following components one at a time, in the order shown,
restarting the blade server each time:
- All optional devices installed in the blade server
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error Code: 0x806F011B Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
System board, interconnect (Scale-Flex cable)
configuration error |
- Reseat the scalable blade complex (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
- Reseat the scalability expansion card (see Removing the 2-node scalability card and Installing the 2-node Scalability card).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
Blade bezel 1, interconnect (Front panel) configuration
error |
- Reseat the operator control panel (see Removing the control panel and Installing the control panel).
- Replace the operator control panel (see Removing the control panel and Installing the control panel).
|
Error |
Interconnect 5 (SideScale Card) configuration
error |
- Reseat the scalable blade complex (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
- Reseat the scalability expansion card (see Removing the 2-node scalability card and Installing the 2-node Scalability card, or Removing the 1-node speed burst card and Installing the 1-node speed burst card).
- Update the firmware for the blade server (see Updating firmware and device drivers).
- Replace the scalability expansion card (see Removing the 2-node scalability card and Installing the 2-node Scalability card, or Removing the 1-node speed burst card and Installing the 1-node speed burst card).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
Interconnect 5 (Unknown Scale ID) configuration
error |
- Reseat the scalable blade complex (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
- Reseat the scalability expansion card (see Removing the 2-node scalability card and Installing the 2-node Scalability card, or Removing the 1-node speed burst card and Installing the 1-node speed burst card).
- Attempt to create the hardware partition again (see Working with a scalable blade complex).
- Update the firmware for the blade server (see Updating firmware and device drivers).
- Replace the scalability expansion card (see Removing the 2-node scalability card and Installing the 2-node Scalability card, or Removing the 1-node speed burst card and Installing the 1-node speed burst card).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error Code: 0x806F012B |
Information |
System mgmt software (Scale Config) software
change detected |
Information only; no action
is required. Note: This event is not be displayed in the advanced management
module event log. However, it is sent for alerts and SNMP traps.
|
Error Code: 0x806F0129 |
Error |
PCI express bus 3, battery (SAS DC Batt) failed |
- Reseat the battery for the storage interface card.
- Replace the battery for the storage interface card.
|
Error Code: 0x806F0207 Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
Group 4, processor (One of CPUs) BIST failure |
- Remove the blade server and ensure the processors are installed
correctly (see Installing a microprocessor and heat sink).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
- (Trained service technician only) Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
Group 4, processor (all CPUs) BIST failure |
- Remove the blade server and ensure the processors are installed
correctly (see Installing a microprocessor and heat sink).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
- (Trained service technician only) Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
Processor X (CPU X Status) BIST
failure [Note X=1,2] |
- Remove the blade server and ensure the processors are installed
correctly (see Installing a microprocessor and heat sink).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
- (Trained service technician only) Replace the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error Code: 0x806F0208 |
Warning |
System board, Power Module (EPOW Fault) predictive
failure |
This warning message generally indicates that
power redundancy for the blade was lost. The non redundant condition
may have subsequently transitioned back to redundant power state.
- Check to see if a power module has been removed or replaced and
ensure the power modules are installed and functioning properly (see
the Installation and User's Guide for your chassis).
- If this warning message is not a result of power redundancy state
changes, and there are no other indications of chassis power issues,
(trained service technician only) replace the system board assembly
(see Removing an IBM MAX5 expansion blade and Installing an IBM MAX5 expansion blade).
|
Error Code: 0x806F020D |
Warning |
Hard drive X (SSD Exp Drive X)
predictive failure [Note: X=1,2] |
Replace the storage drive (see Removing a solid state drive and Installing a solid state drive). |
Error Code: 0x806F0229 |
Information |
PCI express bus 3, battery (SAS DC Batt) absent. |
Information only; no action
is required.
|
Error Code: 0x806F030C |
Error |
Memory device X (DIMM X Status)
memory scrub failed [Note: X=1-16] |
- Refer to TIP H21455 for minimum code level.
- Check the IBM support website for an applicable retain tip or
firmware update that applies to this memory error.
- Swap the affected DIMMs (as indicated by the error LEDs on the
system board or the event logs) to a different memory channel or microprocessor
(see Installing a DIMM - BladeCenter HX5 for memory population sequence).
- Enable all affected DIMMs using the Setup utility.
- If the failure remains on the original DIMM slots, replace the
DIMM that was not moved. If the failure follows the DIMM that was
moved, replace the DIMM that was swapped.
- If the problem occurs on the same DIMM connector, check the DIMM
connector. If the connector is damaged, (Trained service technician
only) replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error Code: 0x806F0313 |
Error |
Chassis (NMI State) software NMI |
A software nonmaskable interrupt (NMI) has been
detected.
- Check the operating system event log for any related errors and
resolve those errors. If you cannot resolve those errors, contact
the appropriate service provider for the software.
- Check the application log for any related errors and resolve those
errors. If you cannot resolve those errors, contact the applicable
service provider for the software.
- Check the IBM Support web page for any service bulletins that
might be related to this problem.
|
Error Code: 0x806F032B |
Error |
System mgmt software (Scale Config) software
incompatibility |
- If this error is occurring on a blade server operating in stand-alone
mode, update the FPGA firmware.
- If this error is occurring on a blade server that is part of a
scalable blade complex operating in single partition mode, make sure
that the firmware for all IMMs and Field Programmable Gate Arrays
(FPGAs) are at the same level in the blade complex.
|
Error Code: 0x806F0409 |
Information |
System board (Host Power) AC lost |
Information only; no action
is required. Note: This event isl not be displayed in the advanced
management module event log. However, it is sent for alerts and SNMP
traps.
|
Error Code: 0x806F040C Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Information |
Group 1, (One of the DIMMs) memory disabled |
- Check the system event log for any memory errors that might be
related to the specified DIMM and resolve those errors.
- Enable the DIMM connector for the specified DIMM using the Setup
utility or the Advanced Settings Utility (ASU) (see Using the Setup utility or Using the Advanced Settings Utility (ASU)).
- Reseat the affected DIMM (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5) and enable the DIMM connector (see step 2).
- Save the settings and exit from the Setup utility.
|
Information |
Memory device X (DIMM X Status)
memory disabled [Note X = 1-16] |
- Check the system event log for any memory errors that might be
related to the specified DIMM and resolve those errors.
- Enable the DIMM connector for the specified DIMM using the Setup
utility or the Advanced Settings Utility (ASU) (see Using the Setup utility or Using the Advanced Settings Utility (ASU)).
- Reseat the affected DIMM (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5) and enable the DIMM connector (see step 2).
- Save the settings and exit from the Setup utility.
|
Information |
Memory device X (MEU DIMM X Status)
memory disabled [Note X = 1-24] |
- Check the system event log for any memory errors that might be
related to the specified DIMM and resolve those errors.
- Enable the DIMM connector for the specified DIMM using the Setup
utility or the Advanced Settings Utility (ASU) (see Using the Setup utility or Using the Advanced Settings Utility (ASU)).
- Reseat the affected DIMM (see Removing a DIMM - IBM MAX5 expansion blade and Installing a DIMM - IBM MAX5) and enable the DIMM connector (see step 2).
- Save the settings and exit from the Setup utility.
|
Error Code: 0x806F0413 Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
Expansion Module X, (BPE4_Y Slot Z) PCI parity errorNote:
- X = Module number
- Y = BPE4 ID (1, 2, 3, or 4). The max BPE4 number is 4,
and there are 2 slots in each BPE4. Module number is based on the
configuration of the BPE4
|
- If you have a PCI adapter in your blade server, verify that the
PCI adapter is supported in the blade server. For a list of supported
optional devices for the blade server, see the http://www.ibm.com/servers/eserver/serverproven/compat/us/.
- Reseat the PCI adapter (see Removing an I/O expansion card and Installing an I/O expansion card).
|
Error Code: 0x806F0507 Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
Group 4, processor (One of CPUs) configuration
error |
- (Trained service personnel only) Remove the blade server and reseat
the processors (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
|
Error |
Group 4, processor (4S CPU) configuration error |
- (Trained service personnel only) Remove the blade server and reseat
the processors (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
|
Error |
Group 4, processor (2S CPU) configuration error |
- (Trained service personnel only) Remove the blade server and reseat
the processors (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
|
Error |
Group 4, processor (All CPUs) configuration
error |
- (Trained service personnel only) Remove the blade server and reseat
the processors (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
|
Error |
Processor X (CPU X Status) configuration
error [Note X=1,2] |
- (Trained service personnel only) Remove the blade server and reseat
the processor (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
|
Error |
Group 4, processor (Missing Boot CPU) configuration
error |
- (Trained service personnel only) Remove the blade server and reseat
the processors (see Removing a microprocessor and heat sink and Installing a microprocessor and heat sink).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
|
Error Code: 0x806F050C Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
Group 1, memory (One of the DIMMs) correctable
ECC memory error logging limit reached |
- Refer to TIP H21455 for minimum code level.
- Check the IBM support website for an applicable retain tip or
firmware update that applies to this memory error.
- Swap the affected DIMMs (as indicated by the error LEDs on the
system board or the event logs) to a different memory channel or microprocessor
(see Installing a DIMM - BladeCenter HX5 for memory population sequence).
- If the error still occurs on the same DIMM, replace the affected
DIMM (as indicated by the error LEDs on the system board or the event
logs).
- If the problem occurs on the same DIMM connector, check the DIMM
connector. If the connector is damaged, (trained service technician
only) replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
Memory device X (DIMM X Status)
correctable ECC memory error logging limit reached [Note X = 1-16] |
- Check the IBM support website for an applicable retain tip or
firmware update that applies to this memory error.
- Swap the affected DIMMs (as indicated by the error LEDs on the
system board or the event logs) to a different memory channel or microprocessor
(see Installing a DIMM - BladeCenter HX5 for memory population sequence).
- If the error still occurs on the same DIMM, replace the affected
DIMM (as indicated by the error LEDs on the system board or the event
logs).
- If the problem occurs on the same DIMM connector, check the DIMM
connector. If the connector is damaged, (trained service technician
only) replace the system-board assembly (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error Code: 0x806F050D |
Error |
Hard drive X (SSD Exp Drive X)
in critical array Note: X=1-2 |
- Replace the storage drive (see Removing a solid state drive and Installing a solid state drive).
- Rebuild the RAID array (see Using the LSI Logic Configuration Utility program).
|
Error Code: 0x806F0513 |
Error |
Expansion Module X, (BPE4_Y Slot Z) PCI system errorNote:
- X = Module number
- Y = BPE4 ID (1, 2, 3, or 4). The max BPE4 number is 4,
and there are 2 slots in each BPE4. Module number is based on the
configuration of the BPE4
|
- If you have a PCI adapter in your blade server, verify that the
PCI adapter is supported in the blade server. For a list of supported
optional devices for the blade server, see the http://www.ibm.com/servers/eserver/serverproven/compat/us/.
- Reseat the PCI adapter (see Removing an I/O expansion card and Installing an I/O expansion card).
|
Error Code: 0x806F052B |
Error |
System mgmt software, (IMM FW Failover) unsupported
software version |
This error occurs when the service processor
(IMM) firmware is corrupted and has reverted to a previous version
of the firmware.
Complete the following steps to correct this
error:
- Check the IBM support website for an applicable firmware update
that applies to the blade server.
- Restart the IMM and verify the IMM is running the correct firmware
level after the firmware update.
For more information about updating the firmware and the
preferred methods, see Firmware Update Best Practices at http://www-947.ibm.com/support/entry/portal/docdisplay?brand=5000020&lndocid=MIGR-5082923.
|
Error Code: 0x806F0607 Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
Group 4, processor (One of CPUs) SM BIOS uncorrectable
error |
- Verify that the latest system firmware is installed (see Updating firmware and device drivers).
- (Trained service technician only) Replace the microprocessors
one at a time (see Removing a microprocessor and heat sink and Removing a microprocessor and heat sink).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
Group 4, processor (all CPUs) SM BIOS uncorrectable
error |
- Verify that the latest system firmware is installed (see Updating firmware and device drivers).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
Processor X (CPU X Status) SM
BIOS uncorrectable error |
- Verify that the latest system firmware is installed (see Updating firmware and device drivers).
- (Trained service technician only) Replace microprocessor X (see Removing a microprocessor and heat sink and Removing a microprocessor and heat sink).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error Code: 0x806F060D |
Error |
Hard drive X (SSD Exp Drive X)
in failed array Note: X=1-2 |
This error occurs because one or more hard drives
in the RAID array have a fault. Perform these steps:
- Check the event log for errors related to hard drive faults. See Event logs for
more information.
- Replace the storage drive that has a fault (see Removing a solid state drive and Installing a solid state drive).
- Rebuild the RAID array (see Using the LSI Logic Configuration Utility program).
|
Error Code: 0x806F070C Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
Group 1, memory (All DIMMs) memory configuration
error |
Make sure that the DIMMs are installed in the
correct order and configured correctly (see Installing a DIMM - BladeCenter HX5). If you
receive this error code for a blade server configuration that includes
an IBM MAX5 expansion blade, multiple DIMMs might have been disabled.
After you replace the mismatched DIMM, make sure that all DIMMs have
been enabled using the Setup utility (see Using the Setup utility) or using the Advanced Settings
Utility (see Using the Advanced Settings Utility (ASU)).
|
Error |
Group 1, memory (One of the DIMMs) memory configuration
error |
Make sure that the DIMMs are installed in the
correct order and configured correctly (see Installing a DIMM - BladeCenter HX5). If you
receive this error code for a blade server configuration that includes
an IBM MAX5 expansion blade, multiple DIMMs might have been disabled.
After you replace the mismatched DIMM, make sure that all DIMMs have
been enabled using the Setup utility (see Using the Setup utility) or using the Advanced Settings
Utility (see Using the Advanced Settings Utility (ASU)).
|
Error |
Memory device X (DIMM X Status)
memory configuration error [Note X=1-16] |
Make sure that the DIMMs are installed in the
correct order and configured correctly (see Installing a DIMM - BladeCenter HX5). If you
receive this error code for a blade server configuration that includes
an IBM MAX5 expansion blade, multiple DIMMs might have been disabled.
After you replace the mismatched DIMM, make sure that all DIMMs have
been enabled using the Setup utility (see Using the Setup utility) or using the Advanced Settings
Utility (see Using the Advanced Settings Utility (ASU)).
|
Error |
Memory device X (MEU DIMM X Status)
memory configuration error [Note X=1-24] |
Make sure that the DIMMs are installed in the
correct order and configured correctly (see Installing a DIMM - IBM MAX5). If you receive this error code for a blade server configuration
that includes an IBM MAX5 expansion blade, multiple DIMMs might have been disabled.
After you replace the mismatched DIMM, make sure that all DIMMs have
been enabled using the Setup utility (see Using the Setup utility) or using the Advanced Settings
Utility (see Using the Advanced Settings Utility (ASU)).
|
Error Code: 0x806F070D Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Information |
Hard drive X (SSD Exp Drive X)
rebuild in progress |
Information only; no action is required. |
Information |
Hard drive X (SSD Exp Drive X)
rebuild complete |
Information only; no action is required. |
Error Code: 0x806F0807 Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Information |
Group 4, processor (One of CPUs) disabled |
- Check the event logs for other related error messages (see Event logs).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
- (Trained service technician) Remove the blade server and ensure
the processors are installed correctly (see Installing a microprocessor and heat sink).
|
Information |
Group 4, processor (All CPUs) disabled |
- Check the event logs for other related error messages (see Event logs).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
- (Trained service technician) Remove the blade server and ensure
the processors are installed correctly (see Installing a microprocessor and heat sink).
|
Information |
Processor X (CPU X Status) disabled
[Note X=1,2] |
- Check the event logs for other related error messages (see Event logs).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
- (Trained service technician) Remove the blade server and ensure
the processors are installed correctly (see Installing a microprocessor and heat sink).
|
Error Code: 0x806F0813 Note: Multiple
events can be displayed for this error code. Be sure to read the message
text to determine the appropriate recovery actions.
|
Error |
Expansion Module X, (BPE4_Y Slot Z) bus uncorrectable errorNote:
- X = Module number
- Y = BPE4 ID (1, 2, 3, or 4). The max BPE4 number is 4,
and there are 2 slots in each BPE4. Module number is based on the
configuration of the BPE4
|
- Update the firmware for the service processor (BMC), BIOS, and
firmware for the advanced management module.
- Reseat the memory DIMMs and any expansion cards (see Removing and replacing Tier 1 customer replaceable units (CRUs)).
- (Trained service technician only) Replace the system board (see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
Group 4, processor (Critical Int CPU) bus uncorrectable
error |
- Remove the blade server and ensure the processors are installed
correctly (see Installing a microprocessor and heat sink).
- Check the event logs for other related error messages (see Event logs).
- Verify that the system is running the latest UEFI firmware (see Updating firmware and device drivers).
- Run the Setup utility (see Using the Setup utility).
- Make sure that both processors are displayed by the system.
- Load the default settings.
- Go to the System Settings menu and make sure the processor
is enabled.
|
Error |
PCI express bus 0 (Planar PCIe Err) bus uncorrectable
error |
- Reseat the blade server (see Removing the blade server from the BladeCenter chassis and Installing a blade server in a BladeCenter chassis).
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
Group 1, memory (Critical Int DIM) bus uncorrectable
error |
- Check the event logs for other memory errors that might occur
(see Event logs).
- Reseat all of the memory modules in the blade server (see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
- Make sure all of the memory is enabled in the Setup utility (see Using the Setup utility). Notice which memory modules
are disabled before you continue to the next step.
- Replace the memory modules that were disabled in the Setup utility
(see Removing a DIMM - BladeCenter HX5 and Installing a DIMM - BladeCenter HX5).
- (Trained service technician only) Replace the microprocessor that
controls the failing memory module.
Note: DIMM connectors 1 through
8 are controlled by the first microprocessor and DIMM connectors 9
through 16 are controlled by the second microprocessor.
See Removing a microprocessor and heat sink and Installing a microprocessor and heat sink.
- (Trained service technician only) Replace the system-board assembly
(see Removing the system-board assembly - BladeCenter HX5 and Installing the system-board assembly - BladeCenter HX5).
|
Error |
Sub-chassis 1, (Critical Int EXA) bus uncorrectable
error |
- Check the IBM MAX5 expansion blade for any lit error LEDs.
- Reseat the IBM MAX5 expansion blade (see Removing an IBM MAX5 expansion blade and Installing an IBM MAX5 expansion blade).
- If the error still occurs, replace the IBM MAX5 expansion blade
(see Removing an IBM MAX5 expansion blade and Installing an IBM MAX5 expansion blade).
|